6/27/2019 6:28 AM | |
Joined: 12/18/2014 Last visit: 5/4/2024 Posts: 32956 Rating: (4073)
|
Hello Picareto, at first welcome to the forum. Here is a possible solution. I hope I understood you correctly. Since you did not write which LOGO! you have exactly and which LSC version, I have set as a hardware device 0BA8.Standard. The address of the analog input for the sensor depends on how many analog inputs are enabled for a base module. AttachmentTank_level_0BA8.Standard.zip (217 Downloads) |
This contribution was helpful to1 thankful Users |
6/27/2019 9:17 AM | |
Posts: 13 Rating: (0) |
Thanks master Ixo65. Yes the module is standard . Later when i come back home i will try it. Thanks again |
This contribution was helpful to1 thankful Users |
6/28/2019 5:03 AM | |
Joined: 12/18/2014 Last visit: 5/4/2024 Posts: 32956 Rating: (4073)
|
I hope the new version meets your requirements. The filling valves (Q3 and Q4) switches now on delayed and off delayed. You have now message texts for changing the setpoints via display. AttachmentTank_level_0BA8.Standard_V2.zip (175 Downloads) |
This contribution was helpful to1 thankful Users |
6/30/2019 4:53 PM | |
Posts: 13 Rating: (0) |
Thank you so much for your atention. Many thanks ixo65 AttachmentTanque_level_charca_furo_hydrokompass7_0BA9.zip (149 Downloads) |
Last edited by: Picareto at: 06/30/2019 17:11:49 |
|
6/30/2019 7:38 PM | |
Joined: 12/18/2014 Last visit: 5/4/2024 Posts: 32956 Rating: (4073)
|
Only the part with with the valves and the new analog threshold trigger.
AttachmentTank_level_0BA8.Standard_V2.zip (139 Downloads) |
This contribution was helpful to1 thankful Users |
6/30/2019 9:37 PM | |
Posts: 13 Rating: (0) |
Thank you master ixo65...i think it will work perfectly. |
This contribution was helpful to1 thankful Users |
Follow us on