(0)| 8/4/2022 7:41 AM | |
|
Joined: 1/21/2013 Last visit: 1/19/2026 Posts: 4410 Rating:
|
Hi pavlovand, here is an excerpt from the manual: DP/DP Coupler is used to interconnect two PROFIBUS DP networks in order to enable the transfer of data between the master of both networks. This means for 5 masters, you would need 10 couplers to enable data transfer between all masters. Or as shown in your illustration, with 4 couplers you will enable master #1 and #3 to #5 a data transfer with master #2. Kind regards |
This contribution was helpful to
|
|
| 8/5/2022 6:45 AM | |
|
Joined: 10/7/2005 Last visit: 1/19/2026 Posts: 3054 Rating:
|
Hi pavlovand if the aim is for Master 1 to communicate with 4 other Masters via DP/DP couplers, you need 4 DP/DP couplers. Your sketch was almost correct and attached is a revised version that will allow this. |
|
Cheers |
|