1/24/2025 10:38 AM | |
Joined: 8/19/2024 Last visit: 9/5/2025 Posts: 1 Rating:
|
Hi everyone, I'm having some troubles updating the firmware from Version 2.0.12 to V2.6 (I've tried 2.6.4 and 2.6.11). The CPU is a 313C-2 DP (6ES7 313-6CF03-0AB0) and following the requirements, a SIMATIC FIELD PG and a MMC with 2MB capacity. https://support.industry.siemens.com/cs/es/en/view/12011632 It's true that SIEMENS recomends a MMC at least 4MB capacity but some of you had achivied the update with the 2MB one, if I understood well. I tried to follow the steps but everytime it shows me the error code 33:279, which refers to a MMC with insuficient capacity. Has anybody had the same issue? Thanks in advance. Silvia. ------------------------------------------------------------------------------------------ |
Last edited by: Silvia_OI at: 01/24/2025 10:42:54Last edited by: Moderator_Lan at: 01/24/2025 11:14:13link optimized Last edited by: Moderator_Lan at: 01/24/2025 11:15:16New subject after splitting |
|
1/24/2025 11:19 AM | |
Joined: 5/12/2006 Last visit: 9/2/2025 Posts: 22709 Rating:
|
the FW File is 4MB so a 2MB Card will not work for this update |