(1)| 11/20/2013 5:07 PM | |
|
Joined: 9/27/2006 Last visit: 1/13/2026 Posts: 12480 Rating:
|
Hello Big John; Mappings are specific telegrams defined for data exchange with Siprotec relays. If data points you require are not in the mapping descriptions, you cannot add them to the mapping, you must select a different mapping (if it exists)after having determined that this one contains the data required. Then you must configure this new mapping in DIGSI and transfer it to the relay, before youprogramthe data exchangein the PLCwith Profibus-DP. Could you check again what specific datapoints you are looking for in the mapping manual, attached?You can find this manual and more in the Siprotec dowload area: http://www.energy.siemens.com/hq/en/automation/power-transmission-distribution/protection/siprotec/?dlsearch=1&fiProductFamily=SIPROTEC%204&fiProductName=-%20General%20Information Hope this helps, Daniel Chartier AttachmentC:\Users\chard2\Documents\PLCs\pdp_7sj6263_e.pdf (570 Downloads) |
Last edited by: dchartier at: 11/25/2013 4:05 PMLast edited by: dchartier at: 11/20/2013 5:09 PM |
|
This contribution was helpful to
|
|
| 11/24/2013 7:41 AM | |
|
Joined: 11/7/2012 Last visit: 7/8/2025 Posts: 67 Rating:
|
Thanks Chartier... I will get back to you as soon as I got more info. |