(0)| 6/17/2014 6:24 AM | |
|
Posts: 1064 Rating:
|
yes you can hook a 230 lamp across phase to phase with out neutral |
| 6/17/2014 8:43 AM | |
|
Posts: 31 Rating:
|
Hi... Thanks for the feedback. Can we gave PH to PH supply to 2 x 36W FLT Light Also....?? Attached here the WR Diagam for the same. Regards, Sariq Salim "Give Res[pect, gain Res]pect"
AttachmentWR_Ph-PH_2x36W.pdf (373 Downloads) |
| 6/17/2014 10:43 AM | |
|
Joined: 11/21/2007 Last visit: 1/8/2026 Posts: 2327 Rating:
|
Hello Sariq Salim Electrically you can operate the 240V AC Lamp or CFLs, you just have to connect your two phases instead of phase and neutral in the original connection ( Not the way you have marked ). However It is recommended from personnel safety point of view. One of the conductors should be earthed ( e.g. if the 240V supply is from a Control transformer, then one phase is usually earthed at the Transfromer end ). Hope this helps Cheers Navnag |
|
There is no such thing as the last bug in a program |
|