10/6/2020 5:18 PM | |
Joined: 12/18/2014 Last visit: 9/15/2025 Posts: 35964 Rating:
|
If you can't switch the ADAM interface to 0-10V, then do it as I suggested. |
10/6/2020 5:26 PM | |
Joined: 12/18/2014 Last visit: 9/15/2025 Posts: 35964 Rating:
|
Extract from the manual: 4.3 ADAM-6017 8-ch Analog Input/2-ch Digital
Output Module The ADAM-6017 is a 16-bit, 8-ch analog differential input module with programmable input ranges on all channels. The module has been designed with eight analog inputs and two digital outputs. The accepted input types are millivolt (±150, ±500, 0~150, 0~500 mV), voltage (±1, ±5, ±10, 0~1, 0~5, 0~10 V), and current (0~20, 4~20, ±20 mA) signals, and data are transmitted to the host computer in engineering units (mV, V, or mA). Each analog channel can be configured to an independent range, thus allowing individual channels to be used simultaneously in different applications. See attachment ... AttachmentADAM-6000_User_Manaul_Ed_9 PDF-page 77.pdf (517 Downloads) |
Last edited by: ixo65 at: 10/06/2020 17:31:03 |
|
Follow us on