Boa tarde. Estou com um problema em uma transfer que usa esse sistema. Sempre que a mesa vai girar, a mesma sai fora de posição e aparece, além disso, a falha 799. É como se a mesa não guardasse as posições que a mesma precisa parar para as operações. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 03/21/2024 11:36:35New subject after splitting |
|
3/21/2024 11:14 PM | |
Joined: 10/17/2007 Last visit: 10/16/2024 Posts: 4046 Rating: (354)
|
Here is Siemens 611U manual saying: Error 799 FEPROM backup and HW Reset required Cause Parameters were re-calculated. Parameters must be saved and the module run up again after this new calculation. Remedy The newly calculated data should be saved in the FEPROM. The new parameters become effective the next time that the module runs up! Acknowledgement POWER ON Stop response STOP II (SRM, SLM) STOP I (ARM)
|