You want to simulate power failure? Please see the attached part of the onlinehelp (3.3.5 , power failure). As long as you press this button you simulate power failure and you can see the reaction after power return. Retentive data will be stored, non-retentive data will not. E.g. a retentive counter will continue counting from the value it had before power failure. A non-retentive counter will start beginning from start value (normally 0). Retentivity you can select by checkbox in each function. If LOGO! was in RUN mode before power interruption, it should be in RUN mode again after power return. If it was in STOP mode, it will be in STOP mode after power return. AttachmentOnlinehelp.pdf (558 Downloads) |