2/13/2019 11:27 AM | |
Joined: 11/8/2017 Last visit: 10/16/2024 Posts: 338 Rating: (191) |
Hi, You can also view and use Slope/Intercept values from a pre-defined list. See attached. In CFC editor, open the 'Edit I/O Addresses' window. Right-click on the Slope or Intercept cell for your 4-20mA device, and select Assign Conversion. This pop-up will list some standard ranges that are used by various Siemens devices. At best, the Min/Max range of your device will be listed here for you to select. At worst, it'll let you understand the concept behind Slope/Intercept. Regards, AttachmentSlopeIntercept.zip (450 Downloads) |
Last edited by: _CJ at: 2/13/2019 11:32:33 AM |
|
This contribution was helpful to1 thankful Users |
2/13/2019 3:47 PM | |
Joined: 12/31/2018 Last visit: 3/10/2024 Posts: 96 Rating: (4) |
Thank You So much for valuable suggestions. Got my answer. |
Follow us on