12/6/2024 10:15 AM | |
Joined: 3/14/2008 Last visit: 9/8/2025 Posts: 2216 Rating:
|
Hi, It looks like the system does not know who is master. Maybe check if you can disable runtime on one of the servers and check if everything is ok. |
If I could help you, you can use the RATE button. Thank you. |
|
12/16/2024 11:28 AM | |
Joined: 1/11/2019 Last visit: 8/14/2025 Posts: 899 Rating:
|
Hello Arun, These alarms are generated from the system generated blocks (You can find them inside the @CFC charts in Chart folder). @CFC charts and there blocks are related to your hardware configuration devices. The predefined time in each blocks for alarm is 15Sec. Try to give the higher time and check once to not to get the alarms frequently. Kindly go through the below link to know about the block I/Os and message texts. Relevant part for your query starts from page number 383 Process Control System PCS 7 Basis Library (V9.0 SP2)Hope it help you! |