1/21/2025 9:18 AM | |
Joined: 3/14/2008 Last visit: 9/11/2025 Posts: 2216 Rating:
|
Hi, It can be two things: - Operator does not have the correct authorization - OS_Perm bit is disabled Please check the block in CFC and under properties, to go the Start I/O and check which OS level is assigned. It can be a number like 1,2,3. Default it set at 1 so the operator with: Process Controlling can press the button. Level 2 is Higer Process Controlling and 3 is Highest Process Controlling If this is not the case, the OS_Perm bit can be disabled (set at 0) so the user in WinCC is not allowed to use the Start command. |
If I could help you, you can use the RATE button. Thank you. |
|
1/21/2025 12:49 PM | |
Joined: 5/21/2013 Last visit: 9/2/2025 Posts: 28 Rating:
|
Very helpful. Thank you |