(0)| 10/22/2025 9:52 AM | |
|
Joined: 11/19/2023 Last visit: 1/20/2026 Posts: 9 Rating:
|
Will it work for MTP unified aswell? |
| 10/22/2025 10:57 AM | |
|
Joined: 1/21/2013 Last visit: 1/22/2026 Posts: 4427 Rating:
|
Hi rafalsky, No, the WinCC Unified Basic Panel does not allow you to transfer the operating system to a USB drive in maintenance mode. For this, you must use ProSave. Setting up the PG/PC interface correctly is a very important step. Kind regards |
| 1/21/2026 9:03 PM | |
|
Joined: 1/21/2013 Last visit: 1/22/2026 Posts: 4427 Rating:
|
Hi AutoGen_9025027, The manual contains all the information needed to perform a factory reset. If this does not resolve the issue, however, it will be difficult to provide further assistance. However, here are some additional notes:
Kind regards |
This contribution was helpful to
|
|
| 1/22/2026 7:43 AM | |
|
Joined: 1/21/2013 Last visit: 1/22/2026 Posts: 4427 Rating:
|
Hi AutoGen_9025027, The image you provided shows that the device is in maintenance mode. This is good, as it means you can begin loading the image. The following are recommended steps to avoid potential problems:
If an error occurs, testing the procedure with a working panel (if available) might be helpful. It cannot be ruled out entirely that your device cannot be reset via Ethernet. If another panel successfully resets, it would indicate an error. In that case, your panel needs to be repaired. Kind regards |
This contribution was helpful to
|
|