6/21/2016 9:49 AM | |
Posts: 8 Rating: (0) |
Or is it not possible? |
6/27/2016 11:08 AM | |
Joined: 6/4/2010 Last visit: 9/30/2024 Posts: 387 Rating: (128) |
Dear forum member, You already mentioned one option for the Synco integration. This would be in fact a KNX OPC server. The second option would be an integration in the S7. You need the 6AV6643-7AC10-0AA1 KNX/EIB2S7 editor and function blocks for the communication to KNX over Ethernet. You may also needs a KNX/IP gateway. For further information please see: https://support.industry.siemens.com/cs/ww/en/view/46374645 Please note that there is a simple operating software for the Synco RMU controllers. You may use this software as an alternative, if do not need an integration into Simatic. See link: Best regards, Albis |