Hello, I think you mean CBC board. This board doesn't have own parameters or possibilities for setting address etc. as this are all parameters at the CU2. So it should be possible to replace it just taking the switches for bus terminating into account. Attachmentop_cbc_d_e.pdf (812 Downloads) |
|