Hello, E01 in combination with V4.1 looks strange. I guess you have this information from SIMOCODE ES commissioning editor online view in TIA Portal which was buggy at this Dialog. At the device you should fide E15 or E16 You can also check it with TIA software at online dialog Online&Diagnostics where you should find the firmware version with 3 digits like V4.1.0 or V4.1.1. If it is not V4.1.1 I highly recommend the firmware update: Description of the SIMOCODE pro V firmware update What you can try quick and easy is a bridge between BasicUnit T1/T2 for Thermistor connection and have a restart. Please let me know if you have success with this. Best Regards Michael |