Is there any solution for this error ? I get the same error description after reseting SIMATIC ET 200SP Open Controller, CPU 1515SP PC2 F, then the SW PLC is not able to change to RUN state anymore. The card type shows, "No memory card", so I try to insert another SMC that is used in the other ET 200SP Open Controller, but it still doesn't work. ------------------------------------------------------------------------------------------ |
Last edited by: The Helping Hand at: 11/29/2023 13:54:12New subject after splitting |
|
11/30/2023 9:23 AM | |
Joined: 8/2/2017 Last visit: 9/25/2024 Posts: 2 Rating: (0) |
Relate to original post. CPU goes into stop mode after a power on cylce. For all those who have the same problem. Error is known and an update to the latest bios version (V0301_0000) must done. https://support.industry.siemens.com/cs/ww/de/view/109743969 |