9/5/2024 5:03 PM | |
Joined: 11/8/2017 Last visit: 11/12/2024 Posts: 341 Rating: (195)
|
Hi, At present, the PXC5 can only integrate a fixed set of Siemens KNX devices via PL-Link (shown on Page 5 of the attached file). There is no traditional S-Mode option available that would let you directly integrate other manufacturer's KNX equipment into the PXC5. You have 2 options: 1. Use a KNX to BACnet/IP router, as you suggest. In general, the router would be configured from the KNX ETS tool. You could then integrate the points that you've created in the router into the PXC5 via BACnet/IP. 2. Use a PXC00-E.D controller with KNX firmware. This is engineered with XWorks and also the KNX to PX tool that is part of the XWorks install. You would however need the KNX ETS backup that contains the 3rd party equipment to import this into the Siemens KNX to PX tool to allow to program the integration. Regardless of the option you use, you will need all of the 3rd party devices to be networked together back to your router / controller, and you will also most likely need to connect a KNX power supply to the KNX bus. Regards, AttachmentA6V14075210_Automation stations PXC5.E24_en.pdf (248 Downloads) |