How to make a Pulse pause logig using APL? I would like to turn the ventilation for 10min every hour. |
| 6/30/2025 2:11 PM | |
Joined: 2/1/2010 Last visit: 12/22/2025 Posts: 218 Rating:
In APL library 9.1+ (maybe even 9.0.x) the "TimeTrig" block (FB1802) can support this function by setting PerMode = 4 and setting the desired minutes after the hour to start the trigger and the other linking/operator inputs needed to make it continuous periodic operation. Then if you have a timed duration, use that trigger to set a pulsed timer or whatever else you need for your motor start/stop logic. |
| 6/30/2025 5:24 PM | |
Joined: 3/14/2008 Last visit: 12/21/2025 Posts: 2232 Rating:
Hi, In addition to RVS.wick's post, you can also use:
The AFP block is easiest to setup, just set a pulse and pause time and you're ready, the PuPa block can create pulse/pause signals permanently or by using a loop count. It has support for 10 groups. So if you have configured groupcount = 5 and loopcount = 2, then all five groups are pulsed/paused twice, one after another.
Last edited by: Oreca at: 06/30/2025 17:26:50If I could help you, you can use the RATE button. Thank you. |
| 7/1/2025 1:15 PM | |
PULSEGEN could work but I would never have considered that. It is typically used for PWM outputs to control from a PID that needs to control pulsed output instead of analog. I think there may be some unexpected results with such a long period but it also could be fine.
I would prefer Oreca's solution of AFP over PULSEGEN. Or using TimeTrig if you want control over exactly when the fan triggers each hour. The real beauty is you can try and adjust based on the actual project requirements. Also just pointing out that 70 minute cycle means your fan turns on 10 minutes later each hour. |