Dear Rishikesh, You are getting a IO access error. You are trying to access a PIW/PQW address that is not present in your hardware configuration. Cross check your program (compare HW configuration and Cross reference ) and make the required changes. Look for address 280. With regards, nandgate.
|
9/11/2013 2:57 PM | |
Posts: 166 Rating:
|
Sir SF fault does not come before Control ON, it comes only after Control ON We have previous PLC backup, compared h/w configuration and Program, we did not find any difference, moreover one of our persons told that a week back there was no SF even after Control ON so v r trying to find out reason for SF after Control ON Regards, M. Rishikesh |
9/11/2013 3:37 PM | |
Joined: 1/21/2013 Last visit: 6/6/2024 Posts: 4620 Rating:
|
Hi What do the wordaddress 280? you can also try selecting the blocks in STEP 7, then press CTRL + ALT + R together, select the occupation of the inputs, outputs, flags, timers and counters, and if you look at the inputs and outputs is occupied the area (MB280-MB281). |
Last edited by: Ste39 at: 9/11/2013 3:55 PMLast edited by: Ste39 at: 9/11/2013 3:38 PM |
|
9/12/2013 6:47 AM | |
Posts: 319 Rating:
|
Dear MRishikesh, Can you post snapshots of Hardware Configuration, Diagnostic buffer and cross reference ? Thanks and regards, nandgate.
|