9/17/2007 3:06 PM | |
Posts: 4 Rating: (0) |
I've got a problem with an installation automated with a 317 cpu. There are 4 DP-stations, 3, 4, 11 and 20. 20 is an SEW Movidrive, the others are ET200M. Station nr.3 or nr3 and nr.4 sometimes fail. The failuredoesn't last longer than about 2seconds. I'd like to knowwhat happens, is it a module that fails or is there a problem with the power supply. Is there a way to find out at all, and if yes, what is that way? AttachmentDiagnose1.zip (611 Downloads) |
Last edited by: koeper at: 18.09.2007 08:00 |
|
9/21/2007 8:52 AM | |
Posts: 32 Rating: (1) |
Hi Or just lower the speed on the profibus to test if there are some changes. /Hans |