12/6/2022 10:45 PM | |
Joined: 12/3/2022 Last visit: 5/17/2023 Posts: 9 Rating: (0) |
Hello I followed the attached instructions, The module only with : X171 connector were NS1, NS2 to be shorted X161 connector were 9,48,112 to shorted X121 were pulse enable 63 to be shorted with Enable voltage 9 and similarly Drive enable 64 to be shorted with 9 enable voltage. Aplly 410V AC 3 phases And i have DC link at +- 590 VDC But no yellow ligth I have two equipments with these symptoms, I wanted to make sure they were good before installing them on my client. Thank you Regards AttachmentChecking procedure of IR-FDD (1).pdf (1104 Downloads) |
12/7/2022 10:07 AM | |
Joined: 4/23/2010 Last visit: 11/14/2024 Posts: 8092 Rating: (878)
|
Based on your above observations, I suggest you to connect I/R module on machine & check. Hope this helps. |
12/9/2022 3:20 AM | |
Joined: 10/17/2007 Last visit: 11/15/2024 Posts: 4074 Rating: (357)
|
I read your posts and other members answers. according to your description, please follow PEASNE2000 suggestion install I/R module to the machine --to see there is no alarams related to this module and machine running with load --OK? I attached I/R module terminal drawing I used or tested more than 100 of I/R modules in the machine system or on the test bench--I never see a module yellow LED is NOT "on" but there is 600VDC output. I had case for opposite --yellow LED is on but there is NO 600VDC out put---module was defective. in Your case I don't think your I/R is 100% good--I suggest NOT use it or tested in the machine system
AttachmentIR_module_terminal.pdf (823 Downloads) |
If you like my comments please |
|
This contribution was helpful to1 thankful Users |