Joined: 9/27/2006 Last visit: 10/3/2024 Posts: 12283 Rating: (2685) |
Hello; The attached screenshot shows the technical description of the Logo 8! module you are asking about. As you can see, it us an analog input module, accepting signals from 0-10 V or 4-20 mA. As such, it will accept sensors (of whatever type, and any manufacturer) that outputs a voltage or current signal, within the stated ranges. To distinguish between them in your program you will need to scale the input analog signal to engineering values (gpm rpm , m/s, degrees C) that represent the physical value you are measuring: flow, speed, temperature... https://support.industry.siemens.com/forum/ca/en/posts/scaling-analog-input/261636 Hope this helps Daniel Chartier |
Last edited by: dchartier at: 03/03/2024 11:39:41 |
|
3/6/2024 12:29 PM | |
Joined: 12/18/2014 Last visit: 10/4/2024 Posts: 33879 Rating: (4214)
|
Take also a look of the electric connection (from the data sheet). |
Last edited by: ixo65 at: 03/06/2024 12:32:46 |
|