5/14/2012 9:29 PM | |
Joined: 1/5/2007 Last visit: 4/7/2023 Posts: 1690 Rating:
|
Hello, the attachment shows you how to limit the analoge output. Input ist scaled as temperature from AM2 RTD... Best regards Betel AttachmentAnalog_proportional_V3 (0BA6).zip (922 Downloads) |
==> Meine TAG-Listen: "deut." |
|
This contribution was helpful to
2 thankful Users |
5/16/2012 6:16 PM | |
Joined: 1/5/2007 Last visit: 4/7/2023 Posts: 1690 Rating:
|
Hello, AttachmentDEMO_speed_controlled_analog_output_V2a.zip (669 Downloads) |
==> Meine TAG-Listen: "deut." |
|
This contribution was helpful to
3 thankful Users |
5/17/2012 11:00 AM | |
Joined: 1/5/2007 Last visit: 4/7/2023 Posts: 1690 Rating:
|
Hello Reza, perhaps you mean this article at the german forum part witterungsgeführte Mischersteuerung - Ausführung ohne Bus Plaese remember my newest version of this typ of controller |
==> Meine TAG-Listen: "deut." |
|
This contribution was helpful to
1 thankful Users |
5/29/2012 9:18 PM | |
Joined: 1/5/2007 Last visit: 4/7/2023 Posts: 1690 Rating:
|
Hello realpower_ir, look at the attachment to find the modified circuit of a colling controller. Please remember a) i am not shure, that this circuit solve your controlling application b) the parameters at the circuit are examples c) The output opens by electro power the valve - and need e mecanical method to close the valce iff Q1 is off. The running time from full close to full open should be 120 s or more Best regards Betel AttachmentDEMO_CoolController_V1.zip (553 Downloads) |
==> Meine TAG-Listen: "deut." |
|
This contribution was helpful to
1 thankful Users |