7/6/2010 4:19 PM | |
Joined: 12/22/2007 Last visit: 2/27/2024 Posts: 52 Rating: (0) |
please change new one micromaster. |
7/9/2010 5:27 AM | |
Posts: 5 Rating: (0) |
Yes, output contactor is installed between vsd and motor. |
7/9/2010 7:16 AM | |
Joined: 7/8/2009 Last visit: 8/5/2024 Posts: 1976 Rating: (477)
|
Well, It is not recommended to use output contactor while using VFD. In your case, you are shutting down motor directly. You are not allowing Drive to Stop Motor first, thats why it detects No Load.. If you want to use that contactor, either you should use OFF2 before operating that contactor or, operate contactor only after VFD stops.. Refer following FAQ for more... Can I switch the output of the drive to the motor on and off using a contactor or isolating switch? Best Regards, Devesh Vithani |
I dont Like people driving Fast, thats the reason I overtake them ;) |
|