Dear all, Thanks for your suggestions. I have used another Simulation software called Modbus View for my TCP client PLC, Now its working well here i am attaching the program for both send & Receive and step by step procedure.(i Think it will be helpful for others) Software TIA V13 for PLC and MB_Client FB for TCP client (Master) https://oceancontrols.com.au/datasheet/ocean/ModbusView_TCP_1.61.zip for TCP server (Slave). I think this is the best modbus simulation software for siemens PLC. PLC Side: Step-1: Please Enter Correct IP Address of Simulation PC in MB_Client Step-2: There are 2 MB_Client FB for send and receive with different CONNECT_ID value. Step-3: Make sure that if any of this FB becomes busy Remove the TRUE of REQ Terminal From That FB. Step-4: For send/Receive 1 real value MB_DATA_Length should be 2. (2 words) PC Side: Step-1: IP address of PC as MB_Client FB IP address. Step-2: Select SLAVE and TCP in Configuration setting. Step-3: Create 2 separate pages for send and receive step-4: Select Input registers and 40001-4 for send & 40011-14 for receive length should be same as MB_Client. Step-5: In Status Bar It should show Master connected then Read coils and Write registers. AttachmentS7 1200 TCP CLIENT.zip (691 Downloads) |