3/8/2024 1:59 PM | |
Joined: 2/1/2010 Last visit: 9/27/2024 Posts: 150 Rating: (71) |
Hopefully you have a (multi) project backup archive that you could restore instead. That would be much easier to deal with, then if you have AS changes just copy the OS from the restored project to the current AS project (MP) and rebuild/repair your netpro connections. Migration of OS project from OS back to ES is more complicated. Doing it like you said using project duplicator will get the files back to the ES, but not embed the project into your MP/project. You'll have to do that manually, maybe you figured it out if you are saying compile failed at S7_connection. To fix that you are going to have to rebuild your netpro connections as if you are making a new project. Since the compiler will probably be confused about existing tag information in the OS project, you might need to manually delete all the tags and connections and let the compiler rebuild them all, or you can see if a Compile entire OS with memory reset works first. |
If my post helped you, please rate. Thanks. |
|