Hi, PLCSim does not support named connections. Instead you need to use a TCP/IP or ISO connection. This means in an existing PCS7 project, you need to recompile the OS with the TCP/IP or ISO connection. PS: Route Control addon relies on named connections and thus you cannot use it with PLCSim. |