I need to connect 5 PT100 sensors to the logo. Can the logo accept 3 AM2 PT100 modules connected to it? |
Last edited by: kdc at: 2/15/2007 8:58 AM |
|
2/15/2007 10:02 AM | |
Joined: 4/24/2006 Last visit: 11/18/2024 Posts: 8770 Rating: (1171) |
Hello kdc, I think it should be possible. See the manual: http://support.automation.siemens.com/WW/view/en/16527461 Chapter 2.1 Best regards, Wizard |
2/15/2007 2:55 PM | |
Posts: 26 Rating: (0) |
Estimated friend: I had on the past the same problem. And the solution that I had used a PT 100 MULTIPLEXER connected to the SIEMENS LOGO. The multiplexer permits to connect 16 PT 100 to the SIEMENS LOGO. Other fact you can use the AM2 PT 100 modul of SIEMENS LOGO, but you need to use more than one unit and the cost it is more important, You can see it in internet www.amess.at 16-Kanal PT100 for Siemens LOGOIf you need more information about of it, send to me a message: |