(0)| 8/18/2022 11:01 AM | |
Joined: 4/28/2009 Last visit: 6/3/2025 Posts: 347 Rating:
Hello, parameters of Drive-CLiQ encoder should be read correctly at drive startup. If no, you can have bad signal cable. Do you have DQ cable with two power supply pins on sides of connector lock? And is the cable in order? Also DQ connector on drive could be faulty, you can check it by another DQ module or motor. And finally there could be broken datas in encoder SMI module. You can try to renew motor and encoder datas in this module. On FCDS download page you can get data for your encoder. Instructions are in attached pdf. With regards Martin AttachmentPrograming DQ module.pdf (1051 Downloads) |