(0)| 4/27/2009 9:40 AM | |
Joined: 1/4/2007 Last visit: 12/16/2025 Posts: 1197 Rating:
Hello duyhungsis, If you have a new Siwarex M module, I recommend you to control the measurement signal of the load cell at the Siwarex M module (pins 17 (SIG+) and 18 (SIG-)). If you have an old Siwarex M module, the module is probably damaged through EMC problems. The error messages “A/D error” and “Control limit exceeded” are typical forEMC problems. Please see also into the abridgement of the Siwarex M manual (attached file) the Corrective Measures of the error messages “Internal Error 4” and “External Error 02”. There you can see, that EMC problems can be the cause of these error messages. Best regardsSiwarexi Attachmenterror_messages.pdf (1054 Downloads) |