7/14/2017 11:11 AM | |
Posts: 206 Rating:
|
Hi Amr, can you send the "Online error report" that you see in the background of your screen shot? The hardware error indicator can have several reasons e.g. load cell broken, load cell wrong connected, internal error (Siwarex M broken) ..................................... If you look in the manual you see the asynchronous errors (chapter 11) these cause the hardware error indicator to get on. https://support.industry.siemens.com/cs/ww/en/view/7787784 In the "Online error report" you see the detailed reason. Regards ABenno |
7/18/2017 8:41 AM | |
Posts: 142 Rating:
|
The same problem has been discussed in below links.hopefully it will helpful for you. |
7/23/2017 10:01 AM | |
Posts: 15 Rating:
|
Dear Amankk, Thanks for your help. i read both but still having problem could you please advice me? Thanks, Amr Albasuni |
9/28/2017 8:18 PM | |
Posts: 15 Rating:
|
this is wiring connection as per Electrical drawing thanks, Amr |
10/9/2017 3:45 PM | |
Joined: 1/4/2007 Last visit: 8/26/2025 Posts: 1190 Rating:
|
Hello Amr Albasuni, You can use the attached S7-program. If the load cell isn’t connected correctly, the red SF-LED is on. Best regards Siwarexi AttachmentSiwa_m.zip (645 Downloads) |
This contribution was helpful to
1 thankful Users |
10/11/2017 3:42 PM | |
Joined: 1/4/2007 Last visit: 8/26/2025 Posts: 1190 Rating:
|
Hello Amr, At first, the red SF-LED of the Siwarex M module has to be OFF. If so, you can use the attached file for a calibration. Best regards Siwarexi Attachmentadjustment.pdf (657 Downloads) |
12/7/2017 4:38 PM | |
Posts: 15 Rating:
|
Dear Sir, kindly see attached file Do you have another Siwarex M module? yes, when i connected SF is off Can you exchange for a test the Siwarex M module? yes Maybe the Siwarex M module is damaged.... How i can repair it, shall i sent to Siemens? Which voltages (unit: VDC) can you measure at the Siwarex M module between the pins: - 19 and 17 ? -5VDC - 19 and 18 ? 48mVDC 0VDC - 20 and 17 ? +5VDC - 20 and 18 ? +5VDC Thanks, Amr Adnan Attachmentadjustment.pdf (633 Downloads) |