Hello, I am experiencing a persistent Modbus TCP communication issue between a Siemens S7-1500 PLC and a MOXA MGate MB3180 gateway, and I would appreciate any advice or confirmation from users who have a similar setup. My setup:
Observed behavior:
I have tested multiple configurations:
None of these combinations changed the result: the PLC always receives exception 0x80A3. Important comparison:
Therefore, the issue seems to be a specific incompatibility between Siemens MB_CLIENT and the MOXA MGate MB3180, not a wiring or addressing problem. My question:
Any confirmation, workaround, or official statement from Siemens or MOXA would be very helpful. Thank you in advance. EDIT: Update with packet-level evidence I would like to add an important observation based on Wireshark analysis. As shown in the attached capture, the Modbus TCP communication is technically correct:
Despite this, the Siemens MB_CLIENT (V6.0) always ends with:
This indicates that the TCP response is received on the network level, but is rejected internally by MB_CLIENT. PLC used: CPU 1512SP-1 PN (ET200SP), FW V4.0 ------------------------------------------------------------------------------------------ |