Please refer the attached sheet. Depending upon your MM440 MLFB number & rating you will find minimum & maximum cable size in table at appropriate supply voltage. From the applicable cable size, termination size can be selected. Or please provide drive MLFB number & nominal input supply voltage here so that appropriate cable & termination size can be found out. HTH. AttachmentMM440 input cable & termination size .pdf (419 Downloads) |
| 6/19/2018 6:40 AM | |
|
Posts: 8092 Rating:
|
Please refer the attached sheet. You can select 35 sq. mm single core flexible copper conductor cable for ground connection. HTH. |