7/20/2023 1:33 PM | |
Joined: 11/12/2014 Last visit: 3/12/2025 Posts: 12 Rating:
|
Hi Everyone, I need to enable the function IP Forwarding on CPU S7-1512SP (firmware v2.9) with CPs7-1542SP (firmware v2.1) using TIA v17 update5. I cannot check the box to enable this option. I don't know if with this hardware configuration this option is forbidden. On the hardware description of the CP1542SP the S7-routing feature seems to be included. Anyone knows something about it? Thank you very much Federico |
7/20/2023 2:06 PM | |
Joined: 1/21/2013 Last visit: 3/14/2025 Posts: 3650 Rating:
|
Hi Federico, To enable IP forwarding you need a S7-1500 V2.8 or higher and:
So it is unfortunately not supported for SIMATIC ET 200SP CPUs, expect the new CPU 1514SP-2. Kind regards |
This contribution was helpful to
3 thankful Users |