Hello, I have one problem with simoreg DC MASTER. The problem is following: when I press start button, motor start running and after 3-4 seconds master drive has tripping without any failure. Then after 3-4 seconds waiting I can start motor again, and simoreg tripp again 3-4 seconds later. Does anybody know wher is the problem? Thank you. |
12/16/2016 9:49 AM | |
Joined: 8/25/2006 Last visit: 3/17/2025 Posts: 2213 Rating:
|
Hello. How the drive is controlled? Via operator panel or via buttons connected to binary inputs? What status is diplayed after tripping? |
12/16/2016 1:29 PM | |
Posts: 6 Rating:
|
Thank you for your answer. The drive is controlled via button, and after tripping i have not any displayed failure. If I set it to P002 it show me actuall RPM. After tripping displayed RPM slowing down. Then I must wait few seconds and start it again. If I holding a start button pressed all the time, after tripping it show me a failure F004. |
12/16/2016 2:24 PM | |
Joined: 8/25/2006 Last visit: 3/17/2025 Posts: 2213 Rating:
|
1. Which buttons you pressed? On operator panel of drive or external buttons connected to binary inputs? 2. Can you check parameter P000 after tripping? What is the value? 3. Does your drive has line contactor? Does this contactor switched-off while tripping? |
12/17/2016 11:06 AM | |
Posts: 6 Rating:
|
To starting of the motor I must press an external start button. I think after tripping the parameter P000 is "--" or "1" , i can't remember exactly, but i'll check that on Monday. Yes, the drive has a line contactor and after tripping this contactor swiched off. |
12/19/2016 8:39 AM | |
Posts: 6 Rating:
|
Hi, I checked parameter P000. When I switch on a main circuit breker, the drive on the parameter P000 showing "o7.0", and when i press start button then showing "1". After tripping the drive showing o7.0 again. |
Last edited by: HRV86 at: 12/19/2016 8:40:43 AM |
|
12/19/2016 10:09 AM | |
Joined: 8/25/2006 Last visit: 3/17/2025 Posts: 2213 Rating:
|
Hello. If you have state o7.0 after tripping it looks like the drive was stopped with Stop button connected to terminal 37. Check the connection of this Stop button. What kind of deceleration you have during tripping? Deceleration with RFG, fast stop or coast stop? |
12/19/2016 11:52 AM | |
Posts: 6 Rating:
|
The external wiring is ok. After tripping the motor slows down by inertia. |
12/19/2016 12:41 PM | |
Joined: 8/25/2006 Last visit: 3/17/2025 Posts: 2213 Rating:
|
Could you upload the schematic of drive and parameter list here? |
12/20/2016 7:16 AM | |
Posts: 6 Rating:
|
Hello, i can upload schematic of drive, but can't upload parameter list because I have not a software for that. The drive has for a long time worked well, and few days ago one thyristor bridge has burned. I have replaced all bridges and after that the drive constantly tripping. The drive parameters are unchanged. |