12/3/2014 6:08 AM | |
Joined: 11/8/2011 Last visit: 3/7/2025 Posts: 387 Rating:
Dear Expert, Thanks for the reply When error is one i am getting status 16#a092 and UNIT what is the value i should set with UNIT for sentron PAC3200???? Find attached Backup Data should be received in the DB11 I checked Sentron PAC3200 with Modscan software i am getting frequency at the 55 address But in PLC i am not getting Data.... Please suggest me waiting for your Positive reply If I change the length and start address i am getting error status 16#a006 Thanks in Advance AttachmentTest_mod.zip (405 Downloads) |
Last edited by: Saggy at: 12/3/2014 6:49 AMLast edited by: Saggy at: 12/3/2014 6:30 AMLast edited by: Saggy at: 12/3/2014 6:27 AM |
12/3/2014 9:23 AM | |
Dear Experts, Thanks for your support Finally Communication working fine i am getting Data in the Data Block from Sentron PAC3200 Information FInd the attached backup file which i have tested and Works fine for Communicating CP343-1 Lean as Modbus TCP Client and Modbus Server as Sentron PAC3200. PLC(Mosbus TCP Client)IP Address 192.168.219.3 Port Number :- 2000 Sentron Power PAC3200(Mosbus TCP Server)IP Address 192.168.219.1 Port Number :- 502 MB7 as Clock Memory M7.7 used for Request Trigger Hope this Helps AttachmentModbus_TCP_Client.zip (480 Downloads) |
Last edited by: Saggy at: 12/3/2014 9:25 AMLast edited by: Saggy at: 12/3/2014 9:24 AM |
2 thankful Users |
10/6/2016 8:34 AM | |
Joined: 4/28/2015 Last visit: 4/19/2025 Posts: 10876 Rating:
Hello, you can start investigate in this topic, of course due your HW cfg what you didn't specified: s7 300 plc and Quantum PLCs TCP / IP communication ? |
With best regards... |