1/10/2022 5:18 PM | |
Joined: 9/27/2006 Last visit: 6/17/2024 Posts: 12260 Rating:
|
Hello Dejrons; Are you familiar with the Profinet function "Module-internal Shared Input / Shared Output" (MSI /MSO)? I believe it could fill your requirements. First look at this extract fro the profinet Functions manual, describing MSI/MSO, this will confirm whether this is what you need: https://support.industry.siemens.com/cs/ca/en/view/49948856/122247580939 Then study this guide to implementing MSI and MSO, especially the section on Configuration in two separate projects: https://support.industry.siemens.com/cs/ww/en/view/109736536 Hope this helps, |
1/11/2022 5:41 PM | |
Joined: 9/27/2006 Last visit: 6/17/2024 Posts: 12260 Rating:
|
Hello Dejons; Sorry, I had missed the IM 153-4 in your netowrk, o youare right, MSI/MSO is not supported. Most Profinet rings are based on MRP, and the fastest reconfiguration time for MRP is 200ms. See the documentation fIle for this Application note for more information: https://support.industry.siemens.com/cs/ww/en/view/109739614 Hope this helps, Daniel Chartier |