Hi, So I guess you are trying to download the CFC program into the CPU? When you have setup a redundant Profinet network, where remote IO is connected to two Profinet networks, then you will need to have an additional license: S7 REDCONNECT. (6ES7653-2CX01-0XE0) See the following link: You will need to have setup two redundant CPU's up and running and this license will be installed on the SEC card of the CPU on both of them. You find more info on how to upgrade the SEC card with the redundant license in the following manual: Process automation with the CPU410 (page 65 on the V9.0 manual) |