12/21/2022 11:33 AM | |
Joined: 10/30/2022 Last visit: 1/4/2023 Posts: 10 Rating: (0) |
0-10V
|
12/21/2022 11:34 AM | |
Joined: 10/30/2022 Last visit: 1/4/2023 Posts: 10 Rating: (0) |
1200–1 · 10⁻⁴ mbar and it measures from 0 to 10 V |
12/21/2022 11:38 AM | |
Joined: 6/11/2019 Last visit: 11/8/2024 Posts: 2313 Rating: (102) |
Hello Luna, Proceed as follows to check for leaks: You use two min/max blocks (mode 3) for this. The first is triggered at the start of the test and saves the pending value. At the same time, a switch-off delay is started for the duration of the test. When the output of this delay falls, you trig the second min/max block. You then subtract both values from each other with a comparator and thus get the pressure loss. Merry Christmas Ella_68 (translate me google) AttachmentSchaltplan1.zip (494 Downloads) |
12/21/2022 12:42 PM | |
Joined: 12/18/2014 Last visit: 11/9/2024 Posts: 34179 Rating: (4256)
|
??? What is this? 1200 mbar? |
Last edited by: ixo65 at: 12/21/2022 12:45:09 |
|
12/21/2022 2:09 PM | |
Joined: 10/30/2022 Last visit: 1/4/2023 Posts: 10 Rating: (0) |
mbar is vacuum pressure. 0,001 bar = 1 mbar
|
12/21/2022 2:15 PM | |
Joined: 12/18/2014 Last visit: 11/9/2024 Posts: 34179 Rating: (4256)
|
It is clear to me that 0.001 bar = 1 mbar. But what is: |
12/21/2022 2:43 PM | |
Joined: 12/18/2014 Last visit: 11/9/2024 Posts: 34179 Rating: (4256)
|
Have you a link to the sensor? |
12/21/2022 3:16 PM | |
Joined: 10/30/2022 Last visit: 1/4/2023 Posts: 10 Rating: (0) |
https://www.buschvacuum.com/nl/nl/products/vactest-dpp-400-dpp-400-d.html
|
Follow us on