Hello, I have connected an analog output from the LOGO to HMI with no problems using the AM2 additional module. i was trying to do the same with the I7 analog connections though but this does not seem to work. I have made a simple program on the LOGO and i can see the inputs on the LOGO display from the I7 input and its working fine. What setting do you need in the Tag table for the HMI to be able to read the I7? I have added the LOGO program and a screenshot of the TIA portal tag table where i need to know the data to be able to make the connection. Thanks AttachmentTia portal v16 tag table.zip (648 Downloads) |
Last edited by: KGray-Cademy at: 03/24/2023 11:09:19 |
|
3/24/2023 11:33 AM | |
Joined: 12/18/2014 Last visit: 9/2/2024 Posts: 33661 Rating: (4183)
|
You have forgotten to take the Ax (amplified) of the analog amplifier B005 in Parameter VM Mapping. |