Can someone help with the CFC configuration of a hand valve please ? I want it to be impossible for an operator in Scada to change the position of the valve, only to be able to visualize its curent position i've tried things like Modliop 1 and Localli 1 but it doesnt change anything, in runtime i can still change to position of the hand valve in runtime tsuanis ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 06/05/2023 05:23:01New subject after splitting |
|
6/5/2023 4:58 AM | |
Joined: 3/14/2008 Last visit: 10/15/2024 Posts: 2111 Rating: (942)
|
Hi, Take a look at the I/O: OS_Perm. It's a 32 bit structure where you can define what is possible for an operator to do. You can find in there if the operator may open the valve, close the valve, reset the valve etc. |
If I could help you, you can use the RATE button. Thank you. |
|