Ihave a S7-300 PLC and one OP7 that configure with profibus communication. PWe have just turn them on and we found OP7 is gonig to up, just show “ Ready for transfer While i press at any key in the keypad, there is nothing happen . I want to get out from Ready for transfer and enter the program of the machine then what should I do? Can you tell me? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 11/13/2023 08:50:08New subject after splitting |
|
11/16/2023 7:50 AM | |
Joined: 8/3/2009 Last visit: 10/11/2024 Posts: 13911 Rating: (1757)
|
Hello ahmed_salah49 If the Project does not start on the panel and the Ready for transfer appears then I would say there is no executable project on this Panel. (the same as after reset to factory settings) I think you have to transfer a project from Protool Here is also a link to the device manual, perhaps it helps: https://support.industry.siemens.com/cs/ww/en/view/1145112 Bye Murof |