I am trying to install a GSD file into Step 7 V5.5 +SP4. This GSD file has been generated in TIA Portal V17 and is for a CPU1511 - This has been sent to me from a system installer. I get the following message - Install GSD File (13:4987). I have attached the log file from the failure too. Is there anything that the system installer needs to do when generating the the GSD files to allow this to be used in my software? AttachmentGSD-Installation.txt (411 Downloads) |
11/28/2023 12:38 PM | |
Joined: 3/11/2019 Last visit: 10/18/2024 Posts: 1622 Rating: (300) |
Hi, the GSD file is for a regular CPU1511, at least according to the logfile. "'Checker, which supports GSD(ML) version 'V2.31', is used for GSD(ML) with version 'V2.35'.'" You need a newer version of SIMATIC Manager with support for GSDML V2.35. ***EDIT*** How do you install a GSDML file and which GSDML file version is released for which version of STEP 7 V5.x?For GSDML V2.35, at least STEP 7 Professional 2017 / STEP 7 V5.6 + Hotfix is necessary. regards sancruz |
Last edited by: sancruz at: 11/28/2023 12:40:08Feedback appreciated, please rate |
|
This contribution was helpful to1 thankful Users |
11/28/2023 12:50 PM | |
Joined: 11/28/2023 Last visit: 5/17/2024 Posts: 2 Rating: (0) |
Thank you. I was thinking that I may need to upgrade to another version. Many thanks for your time and feedabck. |