Have read the System Manual? The error that your are getting is that there is no user power. You can see this in the diagnostics buffer in the CPU. You do not have power (+24V, M) connected to the correct terminals on the X10 terminal block. In the manual you can find out what to do about unused inputs. Link to manual: https://support.industry.siemens.com/cs/us/en/view/109814829 Larry |