4/8/2024 8:26 AM | |
Joined: 8/1/2019 Last visit: 9/17/2024 Posts: 300 Rating: (3) |
How do I export selective CMs? I have PCS7 V9.1 SP2 Already tried according to the manual but it's deactivated, see attached. - Exporting selective CMs, EMs, or EPHs (instances) of a project: Another question: can we also make interconnections and change the block icon numbers using CSV? |
Last edited by: ashadako at: 04/08/2024 08:27:57Last edited by: ashadako at: 04/08/2024 08:28:30Last edited by: ashadako at: 04/08/2024 08:28:57Last edited by: ashadako at: 04/08/2024 09:08:13 |
|
4/8/2024 10:04 AM | |
Joined: 3/14/2008 Last visit: 9/27/2024 Posts: 2098 Rating: (938)
|
Hi, You have selected the plant hierarchy folder, but you have to select the AS project. Then the option is selectable. In the next window, you can set the selection. For your other question: You cannot do this with the CM generator. The header columns are fixed and may/cannot be changed. If you want some of it's functionality, you need to export the current view in the Process Object View/Technological List Editor. I think this will be limited and lot of work. I think you will need PAA (Plant Automation Accelerator) for this. For instance you can also create ACMT (Aggregated Control Module Types). So you can create a ACMT called: "Heating" where you have three CMT's interconnected with each other: A PIDConL, MonAnL and VlvAnL. Then the function is imported in PCS7 as ACMT instance and all interconnections are created.
|
Last edited by: Oreca at: 04/08/2024 10:11:54If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to1 thankful Users |