1/17/2015 10:30 AM | |
Posts: 3 Rating: (0) |
Hello! Have some problem with SIPART PS2. When the setpoint changes from 0% to 60-100% in automatic mode, or the transfer from manual mode to automatic with the setpoints, 60-100%, positioner almost reaches the set point, and then releases the air to the values 40-20%. When the air descends in the case of transition to manual mode, the descent of air is terminated, but if the value is 60-100% after 3-4 seconds the valve starts to close up 40-20%, accompanied by a hissing sound.Some times symbol like "h1" is flashing. In manual mode, the positioner behaves: When you open it up to 60-100% waiting 3-4 seconds then again releases the air to 40-20%, with constant hissing, and the valve slowly closes up 20-10%. Air loss is 2%. Settings were recaptured at the factory and again was initializing. The actuator was connected to a tube from another positioner, worked perfectly. The video attached. AttachmentVID_20150116_155804.zip (496 Downloads) |
1/20/2015 10:30 AM | |
Posts: 3 Rating: (0) |
Hello, thx a lot |