Check which input address the drive has, and add 4 Byte. (when the drive data starts at IW256 the current can be read in IW 260) You have convert the value of IW260 to real and calculate: current = IW260 * p2002 / 16384
|
|
|
2/29/2016 2:47 PM | |
Joined: 5/12/2006 Last visit: 10/14/2024 Posts: 22411 Rating: (3017)
|
Hi, what do you mean with "But the value of current is totaly incoherent."? Christoph |
3/1/2016 9:09 AM | |
Joined: 10/23/2015 Last visit: 10/2/2024 Posts: 165 Rating: (2) |
Hi Huggy,
Thanks |
3/1/2016 9:15 AM | |
Posts: 1529 Rating: (202) |
Please read this reply again...... The value in parameter p2002 (usually 150% of motor rated current) will equal 16384 (4000H).
|
This contribution was helpful to2 thankful Users |