Hi I have a s7-416 CPU (6ES7416-2XK02-0AB0) with CP442-1 RNA (6GK7 442-1RX00-0XE0) and another s7-416 CPU (6ES7416-2XN05-0AB0) with CP 443-1 RNA (6GK7 443-1RX00-0XE0). The CPU program wrote in Simatic manager v5.5 and I want to migrate these CPUs to Tia portal but these are not in hardware catalog of Step7 (Tia portal) and that cannot be replaced with GSDML files according this link. How can I use these CPUs in Wincc professional (Tia portal) without migrate it in Tia portal? |
Last edited by: Moderator_Lan at: 10/15/2024 07:34:19link optimized |
|
10/15/2024 7:16 AM | |
Joined: 3/30/2020 Last visit: 11/12/2024 Posts: 4950 Rating: (1011)
|
There is hope. You will need to configure a proxy that can be a stand-in for the PLC. See the following link: |