6/27/2006 4:05 PM | |
Posts: 28 Rating:
Hi, What do I need (hardware and/or software) to backup the configuration of an OP27M (6AV3627-1JK00-0AX0)? Thx |
6/27/2006 4:39 PM | |
Joined: 4/24/2006 Last visit: 7/12/2024 Posts: 8711 Rating:
Hello, You'll need a PC with a COM port, the software Prosave, you can download with the following link: http://support.automation.siemens.com/WW/view/en/10347815 And a cable: 6XV1 440-2KH32 http://support.automation.siemens.com/WW/view/en/21923977 Best regards, Wizard |
6/28/2006 9:31 AM | |
Evelyne, Like mentioned before: There is no opportunity to get the project out off the panel and change it. You can only make a back up off the project. ![]() There is a PCMCIA slot, You can use it to make a back up off the project. See the manual chapter 9.3 http://support.automation.siemens.com/WW/view/en/1142800 An example off the PCMCIA/Jeida Flash Eprom You can use: 6ES7 952-1KP00-0AA0 (8 MB) The project on the OP27M is a compiled version. The only way to change the panel from OP27M to an OP270 is to start all over again with the project. ![]() Best regards, Wizard |