10/5/2006 11:53 AM | |
Posts: 2 Rating: (0) |
Hi, can I use a LOGO! with a bus module without a S7 PLC? grt Tinus |
10/5/2006 1:19 PM | |
Joined: 4/24/2006 Last visit: 10/14/2024 Posts: 8745 Rating: (1168) |
Hello tinus, What do you mean with Bus module? Best regards, Wizard |
10/5/2006 1:40 PM | |
Posts: 2 Rating: (0) |
i mean a asi or eib/knx module do i need a S7 to work with one of these systems? grt tinus |
10/5/2006 2:21 PM | |
Joined: 4/24/2006 Last visit: 10/14/2024 Posts: 8745 Rating: (1168) |
Hello tinus, When you use the ASI-module, the Logo is a slave on the ASI bus. So you need an ASI master. Thiscan be a S7-PLC. When you use the EIB module,You don't have to use a S7-PLC.I found a manual: http://support.automation.siemens.com/WW/view/en/12166759 Perhaps you'll findsome moreinformation there. Best regards, Wizard |